Fuse Protection for JLD-612 Power Input?

Posted: Sat Oct 16, 2010 9:34 pm
by copelandjc
Should a fuse be placed on the AC power input to the JLD-612 controller? If yes, what value is recommended? My application will be powered by 120VAC 60Hz.

Re: Fuse Protection for JLD-612 Power Input?

Posted: Sun Oct 24, 2010 6:23 am
by Joe
It is going to depend on what the wattage is of your heater. Divide the wattage by 100 to get an approximate current requirement and add a few amps to get to a common fuse size. I use a 15A fuse for a 1000 watt heater and 20A for a 1500 watt heater.