Jld612 reverse temperature reading

Posted: Tue May 01, 2012 10:18 pm
by Wato
I connected a k type probe today to my jld612 unit and the temperature went in the reverse. Up on cooler temp, and down on the warmer temps. I checked my parameters with my other working unit and it is the same, but the readings are opposite.
How can I correct this problem.

Regards.

Re: Jld612 reverse temperature reading

Posted: Tue May 01, 2012 11:43 pm
by richiem
Reverse the leads of the probe connections -- thermocouples have a + and a - and you've got them backwards.

Re: Jld612 reverse temperature reading

Posted: Wed May 02, 2012 6:01 am
by Wato
They are connected properly. The red and white wire with the red connector is on pin 9, and the blue is on 10.
I switched them yesterday however and the temp went in the correct direction, but it did not read correctely to the other pid and a inferred thermometer I have. The temp was at 225f and the pid went up to 165f. Is there a self test for the pid? Because the k type probe is new.

Regards.

Re: Jld612 reverse temperature reading

Posted: Wed May 02, 2012 12:15 pm
by richiem
I'm not doubting that you've done things correctly, but just to be sure, you have set OutY for K thermocouple, yes?

As far as I know, the 612 does not have a self-test routine.

That the K thermocouple is new may not assure that it is working correctly, and there's no simple test for thermocouples except for connecting to an appropriate meter. If you have another K probe, try it.

Re: Jld612 reverse temperature reading

Posted: Wed May 02, 2012 7:59 pm
by Wato
Thats ok, I have set Outy to k, the backward 4 or half of a k.

I have replaced it with the old probe which i changed because it was 10 deg higher all the time, and it worked +10f as usual.

I will switch it with the other unit tomorrow to test the probe.

Regards.

Re: Jld612 reverse temperature reading

Posted: Wed May 02, 2012 10:02 pm
by richiem
OK, then it's a probe issue and you can use the 612's offset correction to get it to read correctly.

Re: Jld612 reverse temperature reading

Posted: Fri May 04, 2012 11:34 am
by Wato
I have searched far and wide for info on the offset correction and no results, so I have to ask. What is the offset correction procedures for the 612?

Re: Jld612 reverse temperature reading

Posted: Fri May 04, 2012 11:55 am
by richiem
The manual, available here at the site, shows that the 0089 initialization loop has a setting for PSb -- probe setting error compensation. Just dial in the degrees of offset you need; I think it should automatically be C or F depending on your choice of reading output.

Re: Jld612 reverse temperature reading

Posted: Fri May 04, 2012 10:58 pm
by Wato
I have swiched the reverse problem probe with the other pid and it has the same problem, therefore the probe is faulty. I have reverted and sticking with the old probe and will use the probe correction function to compensate.

Thanks Richiem.