Controller giving erroneous probe readings
Posted: Sat Mar 31, 2012 5:51 pm
by Blucker
Howdy folks, I have a 612 to SSR to Pt100. It gives a constant PV value without response to ice water nor boiling. A second Pt100 yielded the same results. Is the controller bad? Or is there a programmable correction?
Re: Controller giving erroneous probe readings
Posted: Sat Mar 31, 2012 9:25 pm
by Tech_Marco
How you connect the PT100 probe? One Red, and two Blues ?
Also, did you configure the JLD612 for PT10.0 or PT100?
Marco
Re: Controller giving erroneous probe readings
Posted: Mon Apr 02, 2012 10:30 am
by Blucker
I have the red on 8 and the two blues on 9 and 10. I believe I am configured for the Pt100.
Re: Controller giving erroneous probe readings
Posted: Mon Apr 02, 2012 10:56 am
by Blucker
OK. I was not configured for the Pt100. It is working fine now.